  • Jan 9, 2009, 08:20 PM
    tableclocks
    Humidifier not working
    My new humidifier don't seen to be doing its job honeywell HE120A... its all hooked up right and the wheel is turning with the watwer getting on it... the pad.. but the humtiy in the house is about 16 to 22... the house is all 1 floor 1500 sq ft... gas forced hot air... should it take more then 24 hrs to put humi in the house?
    I have a small portaby humity stat in the living room and I tried it in a few places...
    Thanks for any help... richard
  • Jan 9, 2009, 10:25 PM
    wmproop

    What are you wanting the humidity to be?, are you sure your humidistat is accurate?
  • Jan 9, 2009, 10:39 PM
    KC13
    Is the humidifier installed on the supply air side or the return air side? Is it mounted near an air conditioning coil? If so, does it face the coil fins or the coil tube end?
  • Jan 10, 2009, 06:53 AM
    tableclocks
    Quote:

    Originally Posted by KC13 View Post
    Is the humidifier installed on the supply air side or the return air side? Is it mounted near an air conditioning coil? If so, does it face the coil fins or the coil tube end?

    Supply side... faceing the fins... tks
  • Jan 10, 2009, 06:55 AM
    tableclocks
    Quote:

    Originally Posted by wmproop View Post
    what are you wanting the humidity to be?,,are you sure your humidistat is accurate?

    About 30... no I'm not sue its accurate... this morning I get up and it reads 16 and 70 deg
  • Jan 10, 2009, 06:56 AM
    tableclocks
    Quote:

    Originally Posted by wmproop View Post
    what are you wanting the humidity to be?,,are you sure your humidistat is accurate?

    About 30... tks
  • Jan 10, 2009, 08:33 AM
    tableclocks
    Quote:

    Originally Posted by KC13 View Post
    Is the humidifier installed on the supply air side or the return air side? Is it mounted near an air conditioning coil? If so, does it face the coil fins or the coil tube end?

    It is working but just not doing its job... 6 in bypass is only 30 in or less and I pulled it off to feel the movement of air coming out of it and it did come out... fourced out as you know as the return also pulls it... my portable humitstat is working I'm sure... I put it over a pot of warm water... not hot... warm and it went right up to 33... 100.000 BTU furnace... installed just about the ac coils... fin side... 1500 sq foot house... maybe the humitifier just isn't big enough?
    Thank you... richard
  • Jan 10, 2009, 08:57 AM
    KC13
    Did the humidifier come with any literature stating application guidelines (i.e. square footage)?
  • Jan 10, 2009, 12:01 PM
    tableclocks
    Quote:

    Originally Posted by KC13 View Post
    Did the humidifier come with any literature stating application guidelines (i.e. square footage)?

    Yesssss... of course... good for 2000 sq ft... I have 1500