Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Can I install a 2nd baseboard heater (https://www.askmehelpdesk.com/showthread.php?t=301173)

  • Jan 8, 2009, 09:47 PM
    stephen19690_2
    Can I install a 2nd baseboard heater
    I want to put another 2000 watt/240v baseboard heater in my living room now I have one 2000 watt/240v heater in the room now can I just join on the same thermostate on do I have to run a new line from the panel can I use a 20amp breaker for the 2 of them or would I have to upgrade to a larger size breker is 2/12 wire big enough or not
    Hope some one can help me here
    Thank you
  • Jan 8, 2009, 10:36 PM
    21boat

    They way the wattage works is your only supposed to use 80% of the available wattage in the lines for the safety margin/breaker
    So a single 20mp is 120x20 = 2400 watts. The usable is 19200 watts x two 3,840 usable watts on 240 volt
    Basically a baseboard heater is 250 watts per lineal foot.
    To add 2,00000 to the 2,000 watts there is over the 80% rule. Its over by 160 watts buy code of 80%
    Another line should be added or get a heater a tad smaller
    If you up grade your breaker the wire has to be upgraded also as table shows below.

    No more than 15 feet of heat can be put on a standard 20 amp circuit.
    Based on 250 watts per foot of baseboard heater
    Actual usable amps on your line is 16 amps x 240 = 3,840 and your old and new heater combined is 4,000
    14 gauge / 15 amp = 11 feet heat
    12 gauge / 20 amp = 15 feet heat
    10 gauge / 30 amp = 23 feet heat

    Signed 21 Boat

    If I Helped To Answer Your Question Please Rate My Answer

  • All times are GMT -7. The time now is 07:37 AM.