  • Jan 7, 2009, 11:00 PM
    Somme
    Heat only runs through first cycle after replacing thermostat
    Hi,

    I recently replaced my old thermostat for a Goodman AC system (with electric heat) with a Carrier Edge Programmable Thermostat (Edge). My problem is that after Air handler power off (at the main panel) everything works fine for the first cycle (it comes on as programmed etc, switched off when reaching the right temperature etc.). The problem is that when it should switch on the next time it somehow doesn't work: It will give the impulse-you'll hear it clicking, I even sometimes hear the gear gear up, but within a split second it clicks again and switches it off - any temporary holds are lost and it almost looks like nothing happened. Sometimes the display panel goes black for a second, then comes on with all display signs/messages lit for a moment before displaying the regular program mode again. This process does not throw any breakers out, but when trying to troubleshoot the myself I noticed that simply switching that circuit off and on again will get it to run fine the next time it comes on. I guess the power off must be resetting something?? How come I didn't have those problem with the old thermostat? Any suggestions?

    Thank You!
  • Jan 8, 2009, 10:57 AM
    wmproop

    Double check,, triple check the tstat wiring and the set up mode of the tstat,, get back with us
  • Jan 8, 2009, 09:06 PM
    Somme
    Thank You!
    I did rewire, and make sure that there are no shorts.. I could try to post a picture tomorrow. Another interesting observation: If you manually turn off the heat while it is running, you can turn it back on later and it will do another cycle...
  • Jan 8, 2009, 09:56 PM
    momof2kids
    Quote:

    Originally Posted by Somme View Post
    Thank You!
    I did rewire, and make sure that there are no shorts.. I could try to post a picture tomorrow. Another interesting observation: If you manually turn off the heat while it is running, you can turn it back on later and it will do another cycle...

    You might have to actually PROGRAM the thermostat... try this and let us know...
  • Jan 8, 2009, 10:00 PM
    momof2kids
    Quote:

    Originally Posted by Somme View Post
    Thank You!
    I did rewire, and make sure that there are no shorts.. I could try to post a picture tomorrow. Another interesting observation: If you manually turn off the heat while it is running, you can turn it back on later and it will do another cycle...

    Sorry, I was not finished to the above... Because by turning the thermostat off, you are resetting the thermostat and it goes through cycle 1 and will stall at cycle 2, again...

    OR

    You may have to put a jumper between the "R" terminal and "W" terminal...

    Good luck
  • Jan 9, 2009, 09:25 PM
    Somme
    Wow! Bridging seems to have worked - I connected Rh to Rc with a jumper, I think my old thermostat was set up that way and I should have learnt from it (looked as if they were already integrally connected in the new one?). Anyway, I'll watch it though the next few cycles and see whether the issue returns. Thank You for your help and advice!!
    :):):)
  • Jan 9, 2009, 10:58 PM
    momof2kids
    Quote:

    Originally Posted by Somme View Post
    Wow! Bridging seems to have worked - I connected Rh to Rc with a jumper, I think my old thermostat was set up that way and I should have learnt from it (looked as if they were already integrally connected in the new one?). Anyway, I'll watch it though the next few cycles and see whether the issue returns. Thank You for your help and advice!!!!!!!!!!!
    :):):)

    No problem!! I betcha didn't think that MOMOF2KIDS would have that kind of answer:D:D:D... Just kidding, my husband is an HVAC mechanic and he told me what to type, so I cannot take any credit... I hope it continues to work for you!!

    Good luck...
  • Jan 10, 2009, 02:34 PM
    Somme
    3 Attachment(s)

    Thank You MOMOF2KIDS!

    Unfortunately, after waiting for the next program periods to kick in, it started doing the same thing again. And bridging R and W led to constant "uncontrolled" running of the unit. I attached some pictures of the darn thing (and its official wiring logic, and the display unit while its acting up... )

    Thanks again, and please let me know if you have any other ideas!
  • Jan 10, 2009, 04:22 PM
    KC13
    After installation, did you go through the configuration options to assure they are set correctly for your system type? Check the installation instructions for the list of selections. Press and hold the fan button for 10 seconds to access menu.
  • Jan 10, 2009, 04:56 PM
    hvac1000
    Here is the manual if you would like to download it to keep on the computer.

    http://www.robertsservicecompany.com...9-6BF560582E03}
  • Jan 10, 2009, 05:10 PM
    Somme

    Thank You!

    I looked through all the installer program options and everything seems fine.. even the service test sequence is OK, so somehow the problem seems to be related to the cycles... or second and subsequent cycle start up attempts.. Can anyone give me an idea of the internal logic of that? Manual on-off-on seems to be OK. Switching from heat mode to off does not do a real reset, so I'm still outside flipping the jumper in an out to get it to run properly..

    Hmmpf... close to giving up...
  • Jan 10, 2009, 05:16 PM
    KC13
    Double-check the wiring. Is the orange wire on the C terminal connected to the low voltage common circuit?
  • Jan 10, 2009, 05:23 PM
    Somme
    To be honest - that orange wire was the only one "left" - and after connecting it to C the whole thing came to life (including the display unit). On the previous thermostat it was connected to a terminal labeled O...
  • Jan 10, 2009, 05:24 PM
    KC13
    Quote:

    Originally Posted by KC13 View Post
    Double-check the wiring. Is the orange wire on the C terminal connected to the low voltage common circuit?

    By all means, check this. Could be your whole problem.
  • Jan 11, 2009, 04:21 PM
    Somme

    Bingo!

    The orange wire was the trouble maker... After opening the AHU I could only see that it connects to something outside (?), plus it seemed to have higher Voltage on it... I also found the actual user manual of the existing unit and pulled a new low voltage connection to the Common. So far everything seems to work great. Thank you very much!!