Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   220V Needed? (https://www.askmehelpdesk.com/showthread.php?t=30045)

  • Jul 23, 2006, 10:17 AM
    GeorgiaAC
    220V Needed?
    Hi, all. I am having electrical outlets put in a garage. 8 total. 60 AMP breaker box installed. I have 2 right now that are separate, one for a frig and one for a window AC unit.

    I am thinking about buying a window AC/Heating unit. The specs are below:
    Cooling Capacity 12,000/11,200 BTUs/hr.
    Amps (Cooling) 5.5 / 5.8
    Plug Type T blade (tandem)
    Rated Amps (Receptacle) 15
    Volts, Ttl. Connected Load 230 / 208
    Watts (Cooling) 1220 / 1170
    Watts (Heating) 3500 / 2900

    Is 220 necessary and should I have the electrician put one in?

    Thanks for the advice.
  • Jul 23, 2006, 10:49 AM
    tkrussell
    If you check, I am sure you have typical residential voltage of 240 volts, the unit your are considering is rated 208/230 volts, popular with commercial installations.

    Try to find a similar unit to match the voltage you have.

    If you get something of silmlar size you will need to install a 240 volt 20 amp rated circuit and outlet.
  • Jul 23, 2006, 12:23 PM
    GeorgiaAC
    Forgive me, but I am not very knowledgeable about this. Would this mean that I can have a separate outlet, 20 amps, connected directly from the breaker box, with the T outlet configuration, and be fine with the above unit? Or would I have to get one of the larger appliance connections that I have seen for dryers and ranges?

    Thanks for the help.
  • Jul 23, 2006, 12:31 PM
    tkrussell
    No,as long as the AC only is 20 amp or lower, only a 20 amp outlet is needed.
  • Jul 23, 2006, 01:28 PM
    GeorgiaAC
    Thanks the advice. Appreciate it greatly. :)