  • Jan 6, 2009, 08:01 PM
    rebelsinjin
    Furnace won't ignite-blowing cold air
    Hello all, GMP power vented gas furnace won't ignite-blower is blowing cold air-indicator light is flashing 4 times...
  • Jan 6, 2009, 08:38 PM
    KC13
    Check service label for translation of LED fault code and post here. Look inside blower access panel. Continuous blower operation usually indicates an open limit device.
  • Jan 6, 2009, 09:06 PM
    rebelsinjin
    Quote:

    Originally Posted by KC13 View Post
    Check service label for translation of LED fault code and post here. Look inside blower access panel. Continuous blower operation usually indicates an open limit device.

    Does this mean that a limit switch needs to be replaced?
  • Jan 6, 2009, 09:12 PM
    mygirlsdad77

    Maybe. But it may be as simple as pushing a button on a flame rollout. Have you checked filters lately. There is most likely a reason for limit malfunction
  • Jan 6, 2009, 09:16 PM
    MarkwithaK

    The OP didn't state that the blower was running constantly, just that it was blowing cold. Could just be an ignition failure. Flame sensor perhaps. Need more information to accurately diagnose.
  • Jan 6, 2009, 09:51 PM
    rebelsinjin
    Quote:

    Originally Posted by mygirlsdad77 View Post
    maybe. but it may be as simple as pushing a button on a flame rollout. Have you checked filters lately. There is most likely a reason for limit malfunction

    I actually changed air filter about an hour before we noticed no heat coming out just continuous cold air-blower running non stop
  • Jan 7, 2009, 07:04 PM
    mygirlsdad77

    Just waiting to hear what the code means. You should be able to find it on inside furnace cover or in furnace manual.
  • Jan 7, 2009, 07:11 PM
    KC13
    Quote:

    Originally Posted by rebelsinjin View Post
    I actually changed air filter about an hour before we noticed no heat coming out just continous cold air-blower running non stop

    Was the heat working before you changed the filter?
  • Jan 8, 2009, 12:00 PM
    cyberheater

    Your thermostat isn't set on "run" instead of "auto" is it.

    Just had to ask
  • Jan 8, 2009, 05:49 PM
    MarkwithaK
    Quote:

    Originally Posted by cyberheater View Post
    Your thermostat isn't set on "run" instead of "auto" is it.

    Just had to ask

    You mean "ON" not "RUN"