Hello all, GMP power vented gas furnace won't ignite-blower is blowing cold air-indicator light is flashing 4 times...
![]() |
Hello all, GMP power vented gas furnace won't ignite-blower is blowing cold air-indicator light is flashing 4 times...
Check service label for translation of LED fault code and post here. Look inside blower access panel. Continuous blower operation usually indicates an open limit device.
Maybe. But it may be as simple as pushing a button on a flame rollout. Have you checked filters lately. There is most likely a reason for limit malfunction
The OP didn't state that the blower was running constantly, just that it was blowing cold. Could just be an ignition failure. Flame sensor perhaps. Need more information to accurately diagnose.
Just waiting to hear what the code means. You should be able to find it on inside furnace cover or in furnace manual.
Your thermostat isn't set on "run" instead of "auto" is it.
Just had to ask