  • Jan 6, 2009, 05:49 AM
    jerry007
    To HVAV1000 furnace shuts down
    I also have the same problem and I have read your answer to jojointex about cleaning the flame sensor and will try this BUT my qestion is this
    My sensor is located right under the black pipe feding the gas to thr furnace and by the looks of it it seems hard to remove DOES IT JUST PULL OUT or will I need plylers to unscrew it. Hard to tell and I sure do not want to try and pull it out and find out it unscrews



    Jerry007
  • Jan 6, 2009, 07:41 AM
    hvac1000
    Well jerry007 how about a exact model number and brand name for starters. My crystal ball is still broken.
  • Jan 6, 2009, 08:20 AM
    jerry007
    DUH,

    Sorry was writing this very early and did not think


    Make is a Weather King

    Model 80PJ07EAR01

    Jerry007
  • Jan 6, 2009, 08:40 AM
    hvac1000
    http://216.122.22.11/FetchDocument.a...4-d709ed850fa1


    See this link page 3 That is the best I can do for a picture. If the gas line is really in the way the it will have to be removed for the dervice of the flame sensor but a good mechanic should be able to work around that.

    Link

    http://www.allreds.net/WS2/docs/rhe/80pj_man.pdf
  • Jan 6, 2009, 08:43 PM
    jerry007
    Well it helped some what but I think I had better get a pro to check it out I have look at doing it myself BUT there is not enough room to get to it UNLESS I remove the gas line.

    Again thank you for your time and help

    Jerry007
  • Jan 6, 2009, 11:15 PM
    hvac1000
    Post back with the results.
  • Jan 10, 2009, 10:30 AM
    jerry007
    HVAC1000,


    Yes cleaning the flame sensor off seems to have done it I cleand it myself with a litle sand paper although I did not remove it I was able to reach in and work on it best I could.

    Do have another qustion for you

    I replaced my Thermostat a few months ago with a

    LUXTX1500b Thermostat

    And SOMETIMES it will not kick on the furnace when it calls for it I sometimes have to turn it off than on again to kick the furnace on do you think I need another Thermostat
    And if so WHAT WOULD BE A BETTER ONE to buy than the one I have now. I don't mind paying more for something better if it will work

    Again thank you for your help with the flame sensor
  • Jan 10, 2009, 11:17 AM
    hvac1000
    http://www.luxproducts.com/instrmnlt...TX1500_Web.jpg
    Smart Temp TX1500
    http://www.luxproducts.com/instrmnlt...500E_thumb.jpg
    TX1500E
    Does it look like the first one or the second one?
  • Jan 11, 2009, 08:05 AM
    jerry007
    It looks like the SMART TEMP TX1500
  • Jan 11, 2009, 10:06 AM
    hvac1000
    Here is your install manual. Chech to make sure all the settings are correct.

    http://www.luxproducts.com/ART/suppo..._WebManual.pdf
  • Jan 11, 2009, 10:08 AM
    jerry007
    HVAV1000

    I am so upset know looks like its doing the same thing again there are three burners and the first burner will light up, than either the second one will try to light and won't and than shut down will wait a minute or two and than try again. Sometimes it will light up sometimes it won't. I will turn it off using the Thermostat and turn I back on and find that works most of the time.

    Do you think it's the Thermostat needing replacement or the flame sensor OR perhaps both. The Thermostat is only a few months old and the furnace itself is only two years old
    What do you think?

    Thanks for all your help so far

    Jerry
  • Jan 11, 2009, 10:12 AM
    KC13
    If all 3 burners don't light together, you have a problem with flame carry-over. The burners may have dust build-up that is preventing effective cross-lighting, or the gas pressure is insufficient.
  • Jan 11, 2009, 10:23 AM
    hvac1000
    As KC13 says it could be a burner problem but a bad gas pressure regulator/gas valve can also cause this since it is intermittent in nature. The thermostat will not cause the burners to lite off improperly. A flame sensor just senses the flame a is a safety device to allow the gas valve to stay open so that is not causing the burner lite off problem.
  • Jan 11, 2009, 10:41 AM
    jerry007

    This mat sound stupid (sorry I am not very knowledgeable when it comes to my furnace as you can tell) but is the gas regulator and the gas valve the same thing or are they different.Also how can I tell whih one (if there are different) is ausing the proble.

    By the way I leave in Chicago and this coming wek its going to get REAL cold here.

    Thanks for everything you have done so far

    Jerry
  • Jan 11, 2009, 10:46 AM
    KC13
    Do you have natural gas or LP?
  • Jan 11, 2009, 11:15 AM
    jerry007
    Natural gas
  • Jan 11, 2009, 11:20 AM
    KC13
    The main supply regulator is typically located near your gas meter. The gas control on the furnace also has a built-in regulator for adjusting gas input.
  • Jan 11, 2009, 12:28 PM
    hvac1000
    You need to get a accurate gas pressure reading at the gas valve on the furnace FIRST. Then see if it matches the imput rating on the furnace tag. If not then it will need to be adjusted. While the pressure test equipment is attached to the gas valve the unit can be fired up and then you will see if the pressure moves up or down and if the regulator is doing its job.
  • Jan 12, 2009, 06:30 AM
    jerry007
    Well loks like I will call someone in to try and figure this all out sems to me like a pro would be my best bet at fixing what ever is going on with the furnace.

    Thank you again or all your help

    Jerry
  • Jan 25, 2009, 02:36 PM
    jeaniebird
    Lux TX1500b Thermostat is locked. How do I unlock and reset it?