-   -   Intermittent Code 31 on Bryant Plus 90 (https://www.askmehelpdesk.com/showthread.php?t=298874)

  • Jan 4, 2009, 07:39 AM
    matt63634
    Intermittent Code 31 on Bryant Plus 90
    I have a Bryant 350MAV036080 furnace which sometimes gives me a 31 code on the LED. It will run fine for a few cycles then I'll hear the thermostat click for heat and the furnace won't run. I'll check the code and lo and behold, it's 31. If I leave it alone for about 15 min, it'll kick back on and run fine for a few more cycles.

    I've tried everything: cleaned the condensate trap and the hoses which lead to it, replaced the pressure switch, tested the condensate pump, replaced part of the vent PVC and I still can't get the unit to work 100% of the time. The vent PVC APPEARS to be clear outside. I live in a condo where it's hard to get to the actual pipe. I'm beginning to think it's the control board, does this sound like a symptom of a faulty board? Am I missing something else I should try? Thanks.
  • Jan 4, 2009, 08:06 AM
    taftsj
    I had a 31 code on my Bryant plus 90 - repair guy found air switch not closing- ventor would not run. He put in conversion kit #325878-751 - now works fine!

    John in Stratford ON
  • Jan 4, 2009, 08:34 AM
    matt63634
    Quote:

    Originally Posted by taftsj View Post
    I had a 31 code on my Bryant plus 90 - repair guy found air switch not closing- ventor would not run. He put in conversion kit #325878-751 - now works fine!

    John in Stratford ON

    Thanks. Was your furnace intermittent with code 31 or was it always not working?
  • Jan 4, 2009, 08:45 AM
    taftsj
    It was intermittent at first and then it quit altogether.
  • Jan 4, 2009, 12:54 PM
    matt63634

    Okay, some success (I think). I took the cover off to the blower compartment where the circuit board is, and taped the kill switch down so it would run w/o the cover. After the thermostat clicked on for heat and nothing happened, I wiggled the wiring harness which connects the pressure switch to the circuit board - started right up. I think this is my problem. Now, is it the harness or the circuit board which is bad?
  • Jan 4, 2009, 01:14 PM
    hvac1000
    Remove and replace the wire and connector a few times it might be corrosion
  • Jan 4, 2009, 01:17 PM
    taftsj
    I don't know. My work order says "changed out integrated Bd." So I guess it was the board.

    John
  • Jan 4, 2009, 01:27 PM
    KC13
    I'll bet it is the pressure switch. Try this: next time the LED is displaying 31, nudge the wires where they connect to the p/s. If LED becomes steady, the switch is bad.
  • Jan 4, 2009, 01:28 PM
    matt63634

    Thanks. I've already replaced the pressure switch, and messed with the wires. I think it's fine.