Bryant 395cav error code 31
I have a Bryant CAV395024070 furnace that's taking a code 31. When I run a component test, the inducer motor comes on, sometimes for only a second, sometimes for the proper amount of time, sometimes not at all. The remainder of the components all go through the test no matter what the inducer motor does. When I turn the thermostat on, sometimes the furnace runs, other times only the blower motor comes on and will run until I either turn the thermostat off or lower the set temperature so that the thermostat is satisfied. If I get the furnace to run and it satisfies the thermostat and shuts down, it may come back on as normal the next time the thermostat calls for heat. Other times the inducer motor will start then stop before the igniter glows and you can hear a noise coming from the control board. When this happens I reset the manual reset limit switch (flame rollout switch) and the noise goes away and the furnace will then run as normal. Is the problem with a relay on the ctl. Board?
For code 31 it is... Pressure, Draft Safeguard, or Auxiliary limit (when used) switch did not close or reopened. If open longer than 5 minutes, inducer shuts off for 15 minutes before retry. Check for: ***Proper vent sizing and condensate pitch ***Vent restriction or high winds ***Defective inducer motor or start capacitor ***Defective pressure switch or connections. If it opens after trial for ignition period, blower will come on for 90 second recycle delay. ***Inadequate combustion air supply ***Low inducer voltage ***Disconnected or obstructed pressure tubing The pressure switch has been replaced, I have checked the venting and condensate pitch. It is a new filter and has adequate combustion air supply.
Comment on coldathome's post
Coldathome, I have the same problem with the same furnace, now I need to buy a control board, do you remember where on line you bought this contol board, thanks. [email protected]