Carrier 58ZAV, Turn 120v external sw ON, blower runs 2 minutes, no IDM, no anything els
Carrier Gas Furnace 58ZAV115-16 with replacement Circuit Board ICM 282, which replaced a HK42FZ011 board. Probably installed in 2000 or early 2001.
1. When 120V supplied to the furnace through the "field installed" external switch, the furnace blower motor comes on and runs for about 2 minutes and shuts off. Furnace will remain off after this initial run as long as 120V is supplied. Cycling the 120V supply on and off will repeat the above malfunction.
Error code appears to be 33. 3 slow flashes, followed by 3 quicker flashes.
Error code then changes to 31, after blower motor has cycled off.
New ICM 282 board came with a suggested test sequence. Not able to carry out do to above.
2. Problem occurs with and without thermostat wires attached. Problem was same with original board. Check of all Limit Switches, DSS, FRS's, wiring OK. Checked HSI, FPE, GV solenoid for continuity, OK. IDM runs OK when wired directly to 120V source. Checked wires for correct assembled pin connections in new board plugs, appears OK. Ground to furnace sheet metal frame is good.
3. Replaced 24VAC transformer, thinking that the original's output appeared somewhat low when checked at outputs from CPU. Open circuit trans voltage was Ok. New trans made no difference and instruction sheet w. new Circ Bd claims it is very tolerant of voltage hi/lo conditions.
4. Separated all the wire harness leads and checked while moving them, nothing.
:(