  • Dec 23, 2008, 11:46 AM
    drchef
    Blower not working when a/c is turned on
    I turn on the heater and everything works fine, I turn the fan to ON and everything works as it should, but when I turn the a/c on the only thing that happens is a noise from the unit like fluid running through it however the blower does not start, this is with the blower in the ON position and the heat off a/c switch on OFF, however as soon as I switch to a/c the blower turns off and it makes the same noise mentioned above. I have tried to jumper r-g, r-w, and r-y with the same results
  • Dec 23, 2008, 11:53 AM
    KC13

    What type of thermostat? Sounds like a case of bad switch contacts.
  • Dec 23, 2008, 11:59 AM
    drchef
    Thermostat is a Ritetemp model 8035c. I thought the contacts were bad as well, but when I jumper the contacts at both the thermostat and the unit the same thing happens
  • Dec 23, 2008, 12:03 PM
    KC13

    Okay, give us a li'l more info... system type, brand and model #'s. etc.
  • Dec 23, 2008, 12:08 PM
    drchef
    Lennox Elite Series G24M4/5-100A-12. Gas furnace, not to familiar with HVAC systems, so don't quite know what info you are looking for
  • Dec 23, 2008, 12:17 PM
    KC13

    When you jumpered/un-jumpered R-Y, did you see a rather large/bright spark? If the outdoor unit contactor coil is partially shorted, it could be hoarding control voltage while still functional.
  • Dec 23, 2008, 12:22 PM
    drchef
    It does not spark at the thermostat, but it does at the unit, but I would not call it a large/bright spark
  • Dec 23, 2008, 12:26 PM
    KC13

    Try this: disconnect wire from R at indoor unit, then with R-G jumpered, jump R-Y. What happens?
  • Dec 23, 2008, 12:29 PM
    drchef
    With R disconnected won't I simply be jumping G-Y?
  • Dec 23, 2008, 12:30 PM
    KC13
    Quote:

    Originally Posted by KC13 View Post
    Try this: disconnect wire from R at indoor unit, then with R-G jumpered, jump R-Y. What happens?

    Re-read and follow as posted.
  • Dec 23, 2008, 12:49 PM
    drchef
    At the indoor unit with R disconnected and R-G jumpered, then jumping R-Y the same thing happens, the blower is on with r-g jumpered then when I connect r-y it turns off and the only sound left is the small wooshing sound. The spark you previously mentioned, while I still wouldn't call it big, it is much bigger than than anything I get from r-g
  • Dec 23, 2008, 01:16 PM
    KC13

    I would check the outdoor unit contactor coil - see if it looks burned. The test you just performed is strengthening my "hoarding" theory... disconnect power to outdoor unit first.
  • Dec 24, 2008, 09:43 AM
    drchef
    How do I locate the contactor coil and what does it look like?
  • Dec 24, 2008, 01:38 PM
    KC13

    It is the primary control relay for the outdoor unit. If you disconnect the power supply and remove the control compartment cover, the incoming power supply wires should take you right to it. The coil is the fine winding usually visible near the base. Ideally, a check of the coil resistance and/or amps is the sure thing, but if it appears obviously burned no test is necessary.
  • Dec 24, 2008, 02:21 PM
    wmproop

    Its to cold for a/c
  • Dec 24, 2008, 02:28 PM
    drchef
    That wasn't the question now was it, and how do you know it's too cold do you know where I am?
  • Dec 24, 2008, 02:42 PM
    wmproop

    Smile,be happy,a little humor and Christmas cheer goes a long way,, Baa Humbug, I hate it when people can`t take a joke,, I`ll remember your name in the future,:(:(
  • Dec 24, 2008, 03:11 PM
    KC13
    Quote:

    Originally Posted by drchef View Post
    That wasn't the question now was it, and how do you know it's too cold do you know where I am?

    If it's a/c you're needing right now, I'm jealous...
  • Dec 25, 2008, 12:14 AM
    drchef
    New Orleans-It snowed here for the second time in 30 years and two days later I was in shorts