    greoryg
    Replacing T874R/Q674L with RTH7600D 1006
    I am trying to replace my thermostat and need help.

    my old thermostat is a T874R with Q674L sub. The wiring diagram can be seen here.

    http://customer.honeywell.com/techli...0s/60-1152.pdf

    Page 9, Fig. 14.

    T is not used.

    All other wires are present (W2, G, R, X, Z, K, Y, W1)

    ---------------
    My new thermostat is RTH7600D. The installation instructions are here.

    http://customer.honeywell.com/techli.../69-2206ES.pdf

    ---------------

    I can not figure out the configuation that I need. Any help would be appreciated.

    -Greg
  • Dec 23, 2008, 10:21 AM
    dac122

    Are you having trouble wiring it or configuring the new tstat? Please describe your system (HP, furnace, air handler, etc.)? Manufacturers and models would be helpful.

    Without knowing what you have its hard to tell you how to configure your tstat.
  • Dec 23, 2008, 10:22 AM
    hvac1000
    Here are the directions for your old subbase/thermostat. Just transpose the wiring from the old as posted to the new unit.


    http://customer.honeywell.com/techli...0s/69-0272.pdf
  • Dec 23, 2008, 10:32 AM
    greoryg

    It is a heat pump made by intertherm. I cannot access the model number right now. I might be able to get it when I get home.

    I am not sure about the wiring, My thoughts are

    old=new
    R=R
    Y=Y
    G=G
    X=C?
    Z=L?
    W1=B?
    K=E?
    W2=Aux?

    Am I close?
  • Dec 23, 2008, 01:23 PM
    greoryg

    update:

    This is a revised list after a little more insight...

    old=new
    R=R
    Y=Y
    G=G
    X=C (common)
    Z=unused (LED for Service)
    W1=O
    K=unused (LED for Em. Heat)
    W2=Aux

    Jump E and Aux together.

    Is this correct?
  • Dec 23, 2008, 01:28 PM
    KC13

    Almost... W1-O? A heat pump will require either B or O for the reversing circuit (usually O). Connecting W1 to O will activate auxiliary heat when thermostat is set to cool. Post wire colors that correspond to old.
  • Dec 23, 2008, 01:30 PM
    greoryg

    So, W1 should be B?
  • Dec 23, 2008, 01:33 PM
    KC13

    W1 should not be either O or B. Post wire colors that correspond to old.
  • Dec 23, 2008, 01:37 PM
    greoryg

    R=Red
    Y=Yellow
    G=Green
    X=Black
    Z=Tan/Brown
    W1=White
    K=Orange
    W2=Blue
  • Dec 23, 2008, 01:39 PM
    greoryg
    The reason I say that the W1 is B is because on the diagram it shows it between the Heat Changeover Valve and the rise/fall switches
  • Dec 23, 2008, 01:45 PM
    KC13

    While variations are possible, the orange wire is most commonly used for the reversing circuit (hence the "O" terminal designation). Does your new t-stat have an "O" terminal? It may be combined with "B", look closely...
  • Dec 23, 2008, 01:48 PM
    greoryg

    It has an "O/B" designation.
  • Dec 23, 2008, 01:49 PM
    dac122
    Quote:

    Originally Posted by greoryg View Post
    update:

    This is a revised list after a little more insight...

    old=new
    R=R
    Y=Y
    G=G
    X=C (common)
    Z=unused (LED for Service)
    W1=O
    K=unused (LED for Em. Heat)
    W2=Aux

    Jump E and Aux together.

    Is this correct?

    After looking carefully at both manuals, this is the mapping I'd guess at. To be sure you can wire it up in stages: first just power, then add the fan, then your aux heat only, then your HP. If you can't figure the Hp immediately you'll have aux heat.
  • Dec 23, 2008, 01:50 PM
    KC13

    I would suggest you re-consult with hvac1000 as he has unlimited access to technical references that might reveal something unconventional about your arrangement.
  • Dec 24, 2008, 05:16 PM
    greoryg


    These are pictures of the front panel in my unit.

    http://www.flickr.com/photos/33738050@N08/3133614703/
    http://www.flickr.com/photos/33738050@N08/3133618359/
    http://www.flickr.com/photos/33738050@N08/3134440320/
    http://www.flickr.com/photos/33738050@N08/3134441810/
  • Dec 24, 2008, 05:51 PM
    KC13
    Attachments won't open.
  • Dec 25, 2008, 05:45 AM
    greoryg

    Trying again...

    P1000438 on Flickr - Photo Sharing!
    P1000441 on Flickr - Photo Sharing!
    P1000443 on Flickr - Photo Sharing!
    P1000442 on Flickr - Photo Sharing!
  • Dec 25, 2008, 05:48 AM
    greoryg
    Merry Christmas to you and yours.

    -Greg
  • Jan 4, 2009, 08:56 AM
    greoryg

    Are the photos any help in solving the case?
  • Jan 4, 2009, 10:23 AM
    hvac1000
    Actually I do not see a case to solve. Tape off K and Z and then wire it according to the instructions in the new stat. Then make selections settings for your unit as in O or B? etc. The old subbase drawing shows what the old terminals were used for so just transpose them to the new thermostat.