  • Dec 21, 2008, 12:33 PM
    Fish1231
    Coleman Evcon Furnace #DGAT056BDD
    I have a coleman evcon furnace in my double wide. Yesterday it ran fine, today not so good. I can see the "glow plug" light up and then ignite the unit so there is flame and the blower motor turns on... but after a 2 minute run it shuts back down and the air is less then warm during that 2 minutes. I have been told its my centrifical switch, my heat sensor, a cracked heat exchanger, or the anticipater on the tstat. I have no idea where to begin.

    Also this may be of some relevance, My vent cap on the roof got blown off in the last storm. It has been replaced as of yesterday.

    Please Help... its Sunday... no one open and cold as heck!
  • Dec 21, 2008, 01:00 PM
    Fish1231
    Quote:

    Originally Posted by Fish1231 View Post
    I have a coleman evcon furnace in my double wide. Yesterday it ran fine, today not so good. I can see the "glow plug" light up and then ignite the unit so there is flame and the blower motor turns on...but after a 2 minute run it shuts back down and the air is less then warm during that 2 minutes. I have been told its my centrifical switch, my heat sensor, a cracked heat exchanger, or the anticipater on the tstat. I have no idea where to begin.

    Also this may be of some relevance, My vent cap on the roof got blown off in the last storm. It has been replaced as of yesterday.

    Please Help...its sunday...no one open and cold as heck!

    I should also add that this is a propane furnace
  • Dec 21, 2008, 01:41 PM
    KC13

    Worked yesterday, vent cap replaced, not working today? Here's a good place to start...
  • Dec 21, 2008, 01:44 PM
    MarkwithaK

    Just because it is Sunday does not mean you cannot get on site service. Most service companies do have emergency service. You'll pay a lot more though.
  • Dec 21, 2008, 01:58 PM
    KC13

    Maybe the repair guy from yesterday had the wrong idea of a "cap".
  • Dec 21, 2008, 01:59 PM
    MarkwithaK

    You thinking he left his hat on the flue vent?
  • Dec 21, 2008, 02:09 PM
    KC13

    You know how those damn Buckeyes fans are... wanna leave their mark everywhere!
  • Dec 21, 2008, 02:13 PM
    Fish1231

    Let me re-try typing the events in order since I seem to be semi-illiterate on the computer today.

    Furnace worked fine yesterday, today it didn't, then noticed that the vent cap had blown away and replaced the cap today, still not working. As I said, have been told of many different things it could be, just wondering where to start my process of elimination and I don't have the money to call a tech.
  • Dec 21, 2008, 02:20 PM
    KC13

    Have you checked the air filter lately? If it's clogged the unit will overheat and short-cycle.
  • Dec 21, 2008, 02:22 PM
    Fish1231
    The filter is on the main panel of the door. With the door completely off the furnace still short cycles
  • Dec 21, 2008, 02:42 PM
    KC13

    With so many possibilities, you'll have to bear with seemingly useless suggestions. Troubleshooting starts with the most obvious and progresses from there. Do you know if the unit is equipped with a diagnostic status indicator? This is usually a LED on the main circuit board.
  • Dec 21, 2008, 04:04 PM
    Fish1231
    Yes. The indicator is showing 1 blink every few seconds which indicates ignition failure according to the code sheet on the furnace
  • Dec 21, 2008, 04:12 PM
    KC13

    Based on your original post and the fault code given, it sounds like a dirty/oxidized flame sensor. These are located near main burners, usually look like a steel rod, ceramic insulated, with a single wire. Locate, remove, clean with mild abrasive, re-install and try heat again.
  • Dec 21, 2008, 04:46 PM
    Fish1231

    OK... cleaned the flame sensor with 220 git sand paper and reinstalled... same cycle... 3 tries and then ignition failure code.
  • Dec 21, 2008, 05:02 PM
    Fish1231

    I now have also noticed a faint smell of propane coming from the front of the moduale that the flame sensor is connected to just before flame out.
  • Dec 21, 2008, 05:32 PM
    Fish1231

    Could this be a bad gas cellenoid or a closed valve... or does it seem to be a heat exchanger problem?
  • Dec 21, 2008, 06:15 PM
    KC13

    How many burners? Do they all light? Observe flames from start-up. Do they start straying or blowing around when the blower starts? If so, is the sensor still bathed in flame, or exposed?
  • Dec 21, 2008, 06:23 PM
    Fish1231

    Only 1 burner, if the burner is the piece that glows orange before ignition... and yes the flames do blow around, the sensor isn't totally bathed in flame but there is flame on it so it is semi exposed
  • Dec 21, 2008, 06:27 PM
    KC13
    Quote:

    Originally Posted by Fish1231 View Post
    only 1 burner, if the burner is the piece that glows orange before ignition...and yes the flames do blow around, the sensor isnt totally bathed in flame but there is flame on it so it is semi exposed

    The glow before ignition is the ignitor. The burner(s) produce flame. You may have a leaky heat exchanger. Get it checked by a pro ASAP.
  • Dec 21, 2008, 06:50 PM
    Fish1231

    I was afraid of that. I have been told its time for a new furnace if the heat exchanger gets leaky. So now I'm really screwed but thanks for all your help

  • All times are GMT -7. The time now is 12:01 AM.