Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Heat pump programmable stat (https://www.askmehelpdesk.com/showthread.php?t=293993)

  • Dec 19, 2008, 05:18 PM
    jgarner55
    Heat pump programmable stat
    I have a Lennox Heat Pump and want to install a programmable thermmostat for a 2 stage heat pump. I have a 8 wire hook up. O-G-Y-R-B-Br-Bl-W. Which kind of stat should I get.
  • Dec 20, 2008, 12:36 AM
    KC13

    Umm... I would suggest... a programmable thermostat... for a 2 stage heat pump system. Not sure where I got this idea...
  • Dec 20, 2008, 03:07 PM
    KC13

    Lennox designs and nomenclature tend to be a little different that most, so assumptions are risky. It would appear that most of your terminal designations are standard (O-G-Y-R-W), the other 3 may not be. B is likely a low voltage common circuit, the others may be for indicator lights. Posting the thermostat and indoor unit model numbers may be helpful in clarifying what each circuit represents so as to avoid releasing any "Magic Smoke" or "Warning Sparks".
  • Dec 21, 2008, 09:33 AM
    jgarner55

    My model# is HP26-042-7P
    Serial# 5800F56746
    Wireing is O-orange
    G-green
    Y1-yellow
    R-red
    L-black
    T-brown
    C-blue
    W1-white

    Thank you for anything that will help me
  • Dec 21, 2008, 09:49 AM
    KC13

    Check the black and brown wires at indoor unit, post what terminals they are connected to, or if they are not used at all.
  • Dec 21, 2008, 02:30 PM
    jgarner55

    The brown and black wire are spliced to cable going to outside so I will have to go outside to check termation.