    Hvac blower motor not working
    HVAC blower motor does not come on in either the heat mode, a/c mode. Or fan only mode. However, it comes on in emergency heat mode. Any ideas what might be wrong?
  • Dec 14, 2008, 08:58 PM
    hvac1000
    If the blower runs it is not the motor and must be in the control system. Usually a relay or sequencer.
  • Dec 14, 2008, 09:05 PM
    hvacservicetech_07

    Could be a loose connection at the furnace or the thermostat on the "G" terminal. When you switch to emergency most likely the equipment controls the blower,where as the thermostat does in the other listed options.