Heatpump blowing cold air
I have a Rheem Heatpump and am not getting any heat when I switch it to emergency or set the thermostat high enough for the aux heat to come on. There is only 1 heating element and I have tested its continuity with an ohm meter after switching the fuses off and disconnecting the wires to the elements. I have also tested the high limit thermostat and it is functioning just fine. Is it possible that the element could still be bad? When I reconnect everything and turn the furnace on the heating element sequencer opens up the circuit after about 20 seconds and I can measure current flowing through the heating element. After a couple minutes I then shut everything down, pull the blower assembly out half way and the heating element is too hot to touch. Yet the air is still cold out of the registers. What am I missing? I have sat up there for 20 minutes measuring the current through the element to see if it is cycling but I don't see any kind of interruption in the power. I am completely baffled. Can anybody help? I know I can change the heating element if I have to, but it doesn't seem to be the problem since it is getting hot. At least it is too hot to touch.