  • Dec 13, 2008, 06:12 AM
    PASSERVE
    Gas valve failure Payne PG8MAA042090AAJA
    I replaced the gas valve yesterday morning, by 8 pm the same problem happened. I noticed the circuit board was not flashing any fault codes and was not locking the furnace out. i.e. the ignitor glows and the gas valve circuit energizes for a moment ( with wires attached to gas valve) and then inducer stops for a second and then the sequence starts all over again-- indefinetly ! If I remove the wires from the gas valve the voltage on these wires reads about 25 volts for about 5 seconds then the ignitor goes out and the cycle repeats. I am thinking that the board needs to be replaced. Could the board be taking the valve out ? HELP!!
  • Dec 13, 2008, 08:55 AM
    hvacservicetech_07

    Do the burners ever light?
  • Dec 13, 2008, 11:02 AM
    KC13

    Could be a faulty circuit board. There was a production run of boards (Carrier, Bryant, and Payne) that experienced failure of the solder joints at the square multi-pin receptacle. If you can remove the blower door and tape the interlock switch, run the unit and give the connector plug a wiggle when the inducer cuts out. If you notice this action affecting the inducer operation, you probably have a bad board.
  • Dec 13, 2008, 05:33 PM
    PASSERVE

    I replaced both the gas valve and circuit board this afternoon. Normal amp draw at gas valve, 3 amps, thank for your imput !