Please give me answer
![]() |
Please give me answer
Really?
Assuming you're an engineer in training, I would like to believe that engineers are very detailed in their communications.
Please provide much more detail to your question, as what you have provided is not nearly enough.
Need:
Conductor material
What type of " current load".
Supply voltage
Just for starters.
Hi, I have a new air compressor machine (atlas copco) which is need for operation.
Details:45kw,83amps,415volts.
What is the right conductor size to use if conductor material is copper and machine
Position is 15metres from the power source.
Minimum 50 sq. Mm. Of copper 3 core, pvc insulated cable