    Goodman Furnace Model GMPN060-3 Three Blinks Diagnostics.
    I have a Goodman Furnace Model GMPN060-3. I get three blinks biagnostic code. I changed venter (motor assembly) and pressure switch. Still the same three blinks. Moisture drain path is clean and free of debries. After the new parts, furnace started once, but would not start again -- same three blinks. Reset all power switches and waited overnight for things to reset, but still will not start i.e. three blinks. Blower fan is OK, runs on manual. Replaced new filter.

    When the problem first started the problem was intermitent. Furnace would start only in the morning when everything was cold. When it had gone through one cycle it would not start again but give the three blinks. So I changed the pressure switch (1.19", part B13701-48) and the venter assembly (Fasco 7021-9087) based on inside panel diagnostic guidance.

    Any guidance would be helpful. Thanks.
  • Dec 12, 2008, 04:44 PM
    wmproop

    Have you checked all vent pipe from start to finish for any obstructions?
  • Dec 12, 2008, 06:02 PM
    KC13

    Check the square multi-connector at the main circuit board-unplug and reconnect it a few times to "scrub off" the pins and sockets. I hate to say it, but the circuit board on these units is a real egg-vulnerable to oxidation and premature failure. Also check the exhaust vent for sags and/or trapped water.
  • Dec 27, 2008, 03:42 PM
    justintime
    Thanks for the guidance from this forum. I checked the venting and found blockage due to bee hive (yellow jackets?? ) nest remnants. The furnace pipes exhaust in the back yard where we have a bee problem. Thanks for your feed back and suggestions. It avoided me a costly call from the repair person.
  • Dec 27, 2008, 05:41 PM
    MarkwithaK
    Quote:

    Originally Posted by KC13 View Post
    Check the square multi-connector at the main circuit board-unplug and reconnect it a few times to "scrub off" the pins and sockets. I hate to say it, but the circuit board on these units is a real egg-vulnerable to oxidation and premature failure. Also check the exhaust vent for sags and/or trapped water.

    Goodman basher! :p
  • Dec 27, 2008, 05:44 PM
    MarkwithaK
    Quote:

    Originally Posted by justintime View Post
    It avoided me a costly call from the repair person.

    It may have saved you a service call but you more than likely changed out parts that didn't need to be changed. The money you wasted randomly changing out parts probably would have covered a service tech finding your problem and solving it, the difference is that the route you took just took longer.
  • Dec 27, 2008, 06:16 PM
    wmproop

    I wonder why the yellow jackets picked on a janitrol furnace,, some would say it was the fought of the furnace,, could have happened to any brand but since goodman is second largest un-advertized heating and a/c company in the world, they have more equipment in more homes, so I guess the percentages of something going wrong would be high also,, more red apples than yellow apples,, so more red apples to get chewed on
  • Jan 17, 2011, 04:18 AM
    cmaksymchuk
    So its 5 in the AM here... my little girl was up twice last night for what I thought no good reason... until I realized it was pretty cold in our new house. Thermo was set to 71, house was 65. No experience with furnaces but went down stairs to check. We have a high efficiency keep rite furnace and the diagnostic code was beeping 3 times. The front cover said something about a pressure switch so took off the cover. No idea what to do next, googled

    Quote:

    furnace diagnostic 3 flashes no heat
    This was the first result page in the list. Went immediately outside and cleared a massive snow drift from my furnace air intake (it was completely 100% buried in snow). Turned on my breaker, turned on the thermostat control... regular heartbeat diagnostic code and she's pumpin heat like a hot damn. Can't thank you all enough... the power of people sharing information is enough to keep my family warm tonight.

    Cheers,

    Cory