Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Replace the Breaker? (https://www.askmehelpdesk.com/showthread.php?t=290770)

  • Dec 10, 2008, 06:20 PM
    BenNga
    Replace the Breaker?
    So how do I replace this 10Ka 120/240V breaker since my dryer will not heat and I have replaced all its parts. I think I have to replace the breaker (2 pole - single breaker), because when I tested it with my meter, sometimes I would get 120 readings and other times 230 - 240 readings.
  • Dec 10, 2008, 06:37 PM
    bones252100
    Forget the breaker! If you are getting power at all, the breaker is fine. The breaker simply connects or disconnects. The breaker itself does not control voltage control. The erratic voltage readings reported depends on which legs of the receptacle were being read at the time. It is most likely the problem is still in the dryer. Concentrate on that issue & ask again with dryer model details and what has been done thus far. The electricians are here to help.
  • Dec 10, 2008, 06:56 PM
    stanfortyman
    Where exactly did you test for voltage?

    What "all" parts did you replace in your dryer? And WHY?
  • Dec 11, 2008, 06:06 PM
    tkrussell
    Exactly,

    Quote:

    And WHY?
    Parts changing is not troubleshooting the problem.

  • All times are GMT -7. The time now is 07:20 AM.