  • Dec 2, 2008, 08:09 AM
    ETIFLEX
    How to convert amps to KVA
    I need to know how many KVA is 800 amps at 208V
  • Dec 2, 2008, 08:56 AM
    donf
    166.4 kva

    Addendum:
    I*E= VA/1000 = kVA (800)*(208)/1000 = 166.4 kVA
  • Dec 23, 2008, 04:02 AM
    tkrussell
    This is incorrect:

    Quote:

    Originally Posted by donf View Post
    166.4 kva

    Addendum:
    I*E= VA/1000 = kVA (800)*(208)/1000 = 166.4 kVA


    208 Volt is from a 3 phase system.

    Therefore:

    KVA = (I x E x 1.73) / 1000
    KVA = 287.872
  • Dec 3, 2009, 02:20 AM
    rangabg
    Quote:

    Originally Posted by donf View Post
    166.4 kva

    Addendum:
    I*E= VA/1000 = kVA (800)*(208)/1000 = 166.4 kVA

    :)

    Good Ans
  • Dec 3, 2009, 03:33 AM
    tkrussell
    You don't know what a transformer is by your question posted in the Electrical Forum, and you think the wrong answer is a good answer?
  • Jan 22, 2012, 11:39 PM
    Dhanajaprakas
    SIR,

    We have 1 500kva Gen Set three phase. From this Gen Set Maximum How much amps we can use?

  • Jan 23, 2012, 07:02 AM
    tkrussell
    The formula is:

    KVA= I x E x 1.73/1000

    To complete the calculation, the voltage is needed.