  • Nov 30, 2008, 12:20 PM
    fljrc3
    Short in HVAC System Trane
    I have a short in the low volage circuit in my Trane HVAC system.

    The ceramic fuse pops when I turn the AC or the heat on.

    If I just turn on the Blower motor in manual mode and leave ac and heat in the off position, the fan blows at low speed with no problem.

    As soon as I turn on heat or a/c the blower motor speed increases and then in about 15 seconds the fuse blows.

    I have visually checked as many wires as I can and I do not see any shorts. Any ideas.

    Kind Regards,
    Joe
  • Nov 30, 2008, 12:33 PM
    hvac1000
    More info needed,

    https://www.askmehelpdesk.com/heatin...00-284131.html
  • Nov 30, 2008, 05:05 PM
    fljrc3

    The Airhandler is a ;

    Trane Model# TWE031E13FA1
    Manufacture Date 3/96
    The Outside Unit is a

    Trane Model# XL1400
    SUPER EFFICIENT HEAT PUMP
    Model # TWY018A100A3
  • Nov 30, 2008, 05:32 PM
    hvac1000
    The Airhandler is a ;

    Trane Model# TWE031E13FA1
    Manufacture Date 3/96
    The Outside Unit is a

    Trane Model# XL1400
    SUPER EFFICIENT HEAT PUMP
    Model # TWY018A100A3
  • Nov 30, 2008, 05:52 PM
    hvac1000
    That is a standard unit as far as wiring is concerned but it does have a variable speed motor.

    As with all short circuits the removal of a wire to a component can help track it down. What you might do is to sub the ceramic fuse for something cheaper to do your testing with. I have a 1-2 3-4-5 amp mini circuit breakers I use for testing purposes so I do not have to keep replacing the fuse.

    Many of the variable speed setups do use a signal from the low voltage section of the circuit board. When you say it pops after about 15 seconds that gives whatever is overloading enough time to cause enough draw on the low volt side to pop the fuse. Since the fuse does not go right away this could be a tuff one to figure out. The circuit board also might have a built in time delay and that would allow for the 15 seconds also.

    Outside unit

    http://hvactroubleshooters.com/TRANE...%20SERVICE.pdf

    inside

    http://www.aireng.com/clientuploads/Coils_etc/twe_e.pdf

    I hope these manuals help you find and track down the problem.
  • Nov 30, 2008, 06:08 PM
    fljrc3

    Thanks for the manuals.
    Would a short in any of the components, relays, or fan be the cause for the overload or should the problem only be in the low voltage wiring?
  • Nov 30, 2008, 06:14 PM
    hvac1000
    1 Attachment(s)
    Quote:

    Originally Posted by fljrc3 View Post
    Thanks for the manuals.
    Would a short in any of the components, relays, or fan be the cause for the overload or should the problem only be in the low voltage wiring?


    Anything that has to do with low voltage should be your target. As I said before some variable speed motors have low voltage used with them als. See attached.
  • Nov 30, 2008, 06:30 PM
    fljrc3

    So based on what I have seen and what you have told me, a bad blower and or a shorted wire to the blower motor could overload the low voltage circuit. Right?
  • Nov 30, 2008, 06:49 PM
    hvac1000
    Yes that is a possibility BUT there are other items that could also cause the problem. I was just making you aware of the motor situation. I would isolate the low voltage wires one circuit at a time till the problem is found.
    You could also have a short in one of the low voltage wires going to the outside unit. Sometimes a dog or other animal will chew on those wires outside. You have many items to check/test.
  • Dec 6, 2008, 12:48 PM
    fljrc3
    Ok I have put a short tester on the system and the circuit keeps breaking. I have disconnected the blower and the breaker keeps popping. I am now ready to start disconnecting low voltage wires one at a time to see which wire must have a short. I have the following wires from the thermostat to the air handler, and then out ot the outside unit.

    These are my wires
    B- Blue
    W- White
    R - Red
    T - Brown
    Y - Yellow
    G - Green
    O - Orange
    X2 - Black

    Is there any particular order you would recommend disconnecting them and testing them?
  • Dec 6, 2008, 01:50 PM
    fljrc3
    One more question.

    Do you have a description for these different letters?

    B- Blue
    W- White
    R - Red
    T - Brown
    Y - Yellow
    G - Green
    O - Orange
    X2 - Black

    I am trying to change out the old thermostat
    and it just has the following letters on it.
    Can you show me which one of the above letters coorelate with the ones below?

    Rc/R = 24VAC power supply
    C = 24vac Common
    Y1 = Compressor Stage1
    Y2 = Compressor Stage 2
    W2 = Auxiliary Heat
    E = Emergency
    O = Cool Mode Powered Reverse Valve
    B = Heat mode powered reverse valve
    G = Fan
    L = System monitor
  • Dec 6, 2008, 02:35 PM
    KC13

    Have you tried operating the system in the emergency mode? If the fuse does not blow, your problem is definitely in one of the control circuits to the outdoor unit. Check the contactor(s) and reversing valve at the heat pump for evidence of burned coils.
  • Dec 6, 2008, 03:32 PM
    hvac1000
    You are the on site professional. I have supplied you with all the info I have. Since I am not there I cannot do the testing for you or offer you comments on your ability. As I always tell people. It is your equipment and you are working on it. It is difficult if not impossible to be a back seat driver under these circumstances since I want no responsibility if damages occur.
  • Dec 6, 2008, 03:39 PM
    fljrc3
    I have isolated the short to the yellow wire which goes from the airhandler to the outside unit.

    It is on the Y circuit and it is called the "1st stage compressor wire"

    Any thoughts?
  • Dec 6, 2008, 03:43 PM
    hvac1000
    Yep that is the control wire for the comperssor/fan contactor outside. Could be the coil is shorted. OR other items in the Y control wire circuit.
  • Dec 6, 2008, 04:17 PM
    fljrc3

    I am close guys.

    I traced the yellow wire at the outside unit and I noticed that the yellow wire goes to the side of the MS (look like the contact points). In the schematic however the yellow wire goes to the printed circuit board of the outside unit. Is this an option or an alternative way of wiring the system?
  • Dec 6, 2008, 04:23 PM
    fljrc3
    The MS stands for the "compressor motor contactor".
  • Dec 6, 2008, 04:31 PM
    KC13

    If yer pokin' 'round the outdoor unit, you betta pull out the disconnect or shut off the breaker.
    If you have an ohm meter, check the contactor coil with the wires disconnected. Low or no resistance will blow that fuse. See if da coil looks burnt.
  • Dec 6, 2008, 06:47 PM
    fljrc3

    Ok I tested the resistance across the coil with the wires connected.

    There was 1.8 M Ohms. This is low resistance I believe. Do you know what its resistance should be?
  • Dec 6, 2008, 06:55 PM
    MarkwithaK
    Quote:

    Originally Posted by fljrc3 View Post
    Ok I tested the resistance across the coil withthe wires connected.

    There was 1.8 M Ohms. This is low resistance I believe. Do you know what its resistance should be?

    You need to disconnect the wires to the contactor coil to check it's resistance. The wires being connected will give you a false reading.