Originally Posted by 
letmetellu
				 
			How do you know that it is not the thermostat?
Turn the thermostat off and go to the furnace, take the doors off, now use a piece of tape to tape the door swith so it will have power. 
Now use a temporary jumper wire to connectfrom the W terminal on the low voltage part of the circuit board to the R terminal in the same place. This should make the vent assist blower motor come on. after about 
15 - 20 seconds the hot surfice ignitor should start to glow, another 15 seconds the burners should come on and then 30 to 45 seconds the main blower should come on. 
Now if you will follow this procedure and then let me know what happened maybe I can help you work it out. 
Please respond if this helped or not.