Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Gas Furnace (https://www.askmehelpdesk.com/showthread.php?t=283937)

  • Nov 22, 2008, 01:03 PM
    mac777daddy
    Gas Furnace
    I have an Amana Gas Furnace question. The furnace comes on and the flame starts. It does not appear that the blower ever starts because when I put my hand in front of the vents no air is blowing out. What should I check? This is an AMANA GAS FURNACE 80SV. Thanks
  • Nov 22, 2008, 01:12 PM
    hvac1000
    If the flame stays on and no blower it is usually the fan and limit switch or relay depending upon the setup. It could also be the blower motor. You will have to use a meter to test. The wiring diagram is on the back side of the blower door.
  • Nov 22, 2008, 01:14 PM
    mac777daddy

    There is a little motor that looks to be some sort of fan that spin just above the flame unit. That is spinning. Is there another blower I can check to see if it is working?
  • Nov 22, 2008, 01:19 PM
    hvac1000
    Yes the main blower that blows the air around in your home

  • All times are GMT -7. The time now is 01:58 PM.