Originally Posted by jessechenven
I would like to add a washer hook-up in a utility room that I have. It is on the 1st floor of a 2 story home. Directly above it is a bathroom, so I have hot and cold water lines in the wall. As well as two waste pipes (a 3" from the toilet and a 2" from the sink/shower). I am assuming it is a no-no to just hook-up to the waste pipe because that would not allow for proper venting. Is that correct? What are my options (besides ripping out tons of drywall, tile and roofing to put in a new vent)? What about trailer-home one way vents (*just heard about them, never seen one)?
Thanks,
Jesse