-   -   Over flow Goodman furnace (https://www.askmehelpdesk.com/showthread.php?t=281192)

  • Nov 15, 2008, 09:42 AM
    wiremanha
    Over flow Goodman furnace
    On Goodman furnace GMP N100-4
    When the furnace gase valve comes on the flame rolls out of the chamber, after a while the switch clicks off. So the furnace won't work at all until it is reset.

    Thank You:(
  • Nov 15, 2008, 11:07 AM
    hvac1000
    Call for ON SITE service immediately. You have a very dangerous situation.
  • Nov 15, 2008, 08:43 PM
    MarkwithaK

    Yup. More than likely your exchanger is cracked.