Quote:
I guess I need to answer my own questions.
And I guess if you could you wouldn't be here asking us.
1)
Quote:
Do I need to adjust the cut in/out range down, and the cut off maximum up?
I would adjust the cut in point back to 30 PSI and the cut out point up to 50 PSI. Do you need instructions on how to do this.
2)
Quote:
Do I need to adjust the Amtrol pre-charge?
The bladder tank pressure's set at 2 PSI below the cut in point of the control box when the pumps is shut off and the pressure's bled off.
3)
Quote:
What causes the momentary activation of the pump
This could be caised by a faulty check/foot valve. Look at your pressure gage when the pump pumps up to pressure and shuts off. Is there a pressure drop?
4)
Quote:
]why does it need to be manually switched on?
Are you saying the control shuts it down and you have to close the contacts manually or does the pump through the breaker and you have to reset it? Let me know, Tom