Apparently no power at the transformer - is there a fuse somewhere. Model UCG 100-ER
![]() |
Apparently no power at the transformer - is there a fuse somewhere. Model UCG 100-ER
No power going into the transformer means you have a bad fuse or kicked breaker,, if there power going in but none comeing out (24 volts) meaning a bad transformer,, if it's a gas furnace make sure the puch-in door switch is pushed in when checking it out
Is there likely to be a fuse interior to the furnacne - that is other than the CB at thepanel?
This began with a thermostat replacement where the old stat was removed without noting the wirign so I am guessing and am confused by the blue wire but connecting it to blue connection - could I have blown the transformer? We have power into the transformer (120V) and none out on G to R check, so I will change transformer but worried about blowing it again if the stat isn't correct.
Some, if not most, furnaces will have a 3 or 5 amp auto-style fuse on the board. Give that a looking. If you have 120VAC supply at the furnace then your breaker is not tripped. Double check your stat wiring first then replace the x-former.
Kick the breaker off anytime you are working on ,replacing tstat or transformer,, is the safe way
But yes its time to replace transformer for certain