    Honeywell CT47A 4447 Thermostat Fan
    Hello,

    My question is about my thermostat. The thermostat works fine. The furnace cycles normal... It calls for heat when it should and the blower motor operates when asked. Only thing I have a problem is... While everything is good with the fan on "Auto".. When I switch it to "Manual On".. to circulate the air in the home while furnace is off.. the blower does not come on. Any help would be appreciated. There is obviously power to the motor since it does operate on "Auto" but not on Manual. Maybe Tstat?

    Thanks!

    :)
  • Oct 26, 2008, 09:22 PM
    hvac1000
    The green wire controls the blower in the on mode. There is also usually a relay that turns the blower on in the on mode. It is probably the relay but check to be sure you have 24 volts on the green wire to common in the furnace.
  • Oct 27, 2008, 06:13 AM
    KISS

    In HEAT mode, the furnace controls the fan, not the tstat.