  • Oct 20, 2008, 10:01 AM
    zenbones
    Goodman gmp board blinks three times
    Blinks three times

    My goodman furnace does not ignite the HSI, and the board blinks three times. Is this the pressure switch or rollover, or perhaps something else
  • Oct 20, 2008, 10:06 AM
    zenbones

    My furnace is a Goodman GMP 100-3
  • Oct 20, 2008, 10:51 AM
    hvac1000
    3 blinks is end switch closed without inducer on.

    Check venter end switch.

    Also see the back of the blower for a wiring diagram with the blink codes listed.
  • Oct 20, 2008, 11:11 AM
    zenbones

    I changed the pressure switch, and still got the three blinks. So I disconnected the tube and sucked on it to close the pressure switch, causing it to ignite the HSI. The inducer is running but apparently not creating a vacuum to the pressure switch. Could this be clogged? Do I need to take off the inducer and clean that port?
  • Oct 20, 2008, 11:36 AM
    hvac1000
    Could this be clogged? Yes but you might check the connecting tube for cracks first.
  • Oct 20, 2008, 02:43 PM
    zenbones
    As it turns out, the inducer on the unit itself was not working. There was a secondary inducer that was causing it primary inducer to spin, but it was not coming on. I have changed the primary inducer, and now cannot get the primary inducer to work. What is the line voltage on the primary inducer. I am reading around 5vac between the white and black lines. What should it be.
  • Oct 20, 2008, 03:12 PM
    hvac1000
    If I am not mistaken the inducer runs on 120 volts. How about posting a correct model number so we can check.
  • Oct 20, 2008, 03:18 PM
    zenbones
    The model number is GMP 100-3, and it is about 10 years old
  • Oct 20, 2008, 04:46 PM
    hvac1000
    120 volts is the answer I found
  • Oct 20, 2008, 04:57 PM
    zenbones
    When I pull the wires off the vent motor mounted on the furnace, I measure about 5vac between the black and white wires. So would the problem be in the circuit board? According to the schematic, I should read 120vac. In the schematic, there is also a power vent relay. Is that on the board?
  • Oct 20, 2008, 07:11 PM
    hvac1000
    In the schematic, there is also a power vent relay. Is that on the board?

    Yes and it is possible it is defective.
  • Oct 21, 2008, 06:34 AM
    zenbones
    If that is on the board, and defective, does that mean I have to replace the whole board?
  • Oct 21, 2008, 09:38 AM
    hvac1000
    If that is on the board, and defective, does that mean I have to replace the whole board?

    Usually that is the solution since the relay is usually soldered to the board and not easily found at radio shack.
  • Oct 22, 2008, 02:51 PM
    zenbones
    Usually that is the solution since the relay is usually soldered to the board and not easily found at radio shack.[/QUOTE]

    Replaced the whole board, and now enjoying heat once again. Thanks for all your help, you have been great.