Goodman furnace won't stay lit
I have a goodman furnace that goes like this.
Inducer fan comes on, 10 secs later glow lights up,
10 secs later get blue flames
10 secs later blue flames goes out. Repeats 3 times
I have replaced the flame sensor still same problem
But here is the thing. I am only getting 10 volts to the first rollout sensor before it calls for gas. Then when it calls for gas and lights it goes to 0.00
I have also jumped the pressure switch and that didn't cure the problem. I also removed the exhaust vent (just to see if it would run with it disconnected making sure there where no obstructions in chimney) didn't fix the problem.
I have boiled it down to a board or gas valve. Wouldn't it have to be the board since I am only getting 10 volts to the valve and rollouts?