  • Oct 11, 2008, 07:40 AM
    Sadielou
    New modular home,200 amp,under ground condiut.
    We are putting in a mondular home for my daughter and soninlaw.We are going underground from our pole 450 ft to the home.The home has a propane furnace and a 2 ton heatpump (lenox).What size cable do we need and cooper or aluminium.I've been told to different cables so far.We are in British Columbia if that makes a difference for code.The home has a 200amp panel
  • Oct 11, 2008, 07:53 AM
    Sadielou
    New modular home,200 amp,under ground condiut.
    We are putting in a mondular home for my daughter and soninlaw.We are going underground from our pole 450 ft to the home.The home has a propane furnace and a 2 ton heatpump (lenox).What size cable do we need and cooper or aluminium.I've been told to different cables so far.We are in British Columbia if that makes a difference for code.The home has a 200amp panel
  • Oct 11, 2008, 08:17 AM
    stanfortyman
    Your power company will have to tell you this.

    What you are doing is NOT(!! ) a DIY project.

    You will most likely have to have primary wire to a ground transformer and then secondary to the house because of the distance.

    PLEASE calla couple of electricians to get some bids to have this done by a contractor.
  • Oct 11, 2008, 08:17 AM
    stanfortyman

    Double post

    Go here:
    https://www.askmehelpdesk.com/electr...ut-268159.html
  • Oct 11, 2008, 08:21 AM
    Neilcathy67

    We have just done a similar installation. Copper would be to expensive, so AL is the way to go. I would consult your local supplier of Elec. as they would not allow us to do the work, but had to hire an approved contactor and I believed he used # 6 or #4 wire
  • Oct 11, 2008, 09:19 AM
    stanfortyman
    Quote:

    Originally Posted by Neilcathy67 View Post
    I believed he used # 6 or #4 wire

    I hope NOT for a 200 Amp service! :eek:
  • Oct 11, 2008, 11:07 AM
    Sadielou

    I had 2 quotes.I contractor said I could use AL. The EL contractor I used to wire our house said noway for AL because it was to far,450 ft to the modular copper only even though it way more money.He said he used his computer program to do the calculations.I just don't know who to trust.
  • Oct 11, 2008, 01:15 PM
    Neilcathy67
    This was older southern home and it was only 100 amp, but they had me hire a contractor with a ditchwitch to bury the cable.
  • Oct 11, 2008, 01:55 PM
    stanfortyman
    The second guy I would not trust. From the little you just wrote it sounds like he needs some help with this stuff.

    AL or CU has NO bearing on distance, other than the fact that AL would have to be larger than CU for a given amperage. Maybe he is figuring on upsizing the wire for the distance so he thinks the AL would be too large? I doubt it.

    450' is a LONG way to go with secondary!
  • Oct 11, 2008, 01:56 PM
    stanfortyman
    Why not continue this here so there are not two of the same threads running:
    https://www.askmehelpdesk.com/electr...ml#post1316403

    Maybe a mod can lock this one.
  • Oct 11, 2008, 06:16 PM
    Sadielou

    We have 5 acres,so from our secondary to the site for the modular is 450 FT.Still the unanswered question is,what wire can be used with a heatpump and propane furnace 200 amp service on that distance? Hydro will heavy up the wire to our pole.So can AL be used,what size,or does it have be copper?