    Insulating new cement garage floor
    We are going to build a 3 stall garage attached to the house by a breezeway. The ground level had to be built up 4' to match house entry level. The footings have been poured and the interior area filled with sand/gravel. The exterior footing wall banked with clay/dirt mix. The footings were not insulated. The garage is going to be heated. If we put down a water barrier and foam sheeting before the cement floor is poored will this be adequate? Or will the frost move up the banked footing wall and cause problems inside the garage?
  • Oct 9, 2008, 09:38 AM
    ballengerb1

    Where do you live?
  • Oct 9, 2008, 10:38 AM
    Farmer62
    We live in NW Iowa.
  • Oct 9, 2008, 10:49 AM
    ballengerb1

    Does get a bit nippy out there doesn't it. Your footings are in and the sand and gravel are down so your space is limited. You can add a sheet of rigid foam covered by your vapor barrier before you pour but you still want at least 5" of concrete, do you have that much space? Insulation in the walls and most importantly the ceiling will give you the most bang for the buck.
  • Oct 9, 2008, 11:01 AM
    Farmer62
    There is approx. 10 inches from the top of the sand to the top of the footing. And yes, it does get nippy here.
  • Oct 9, 2008, 03:22 PM
    ballengerb1

    Almost sounds like you need a 2" foam board and some additional sand unless you need a beefy floor for heavy equipment. 5" is generally used for a residential garage. I'm just over the IL border east of Dubuque.
  • Oct 14, 2008, 07:48 AM
    Farmer62
    We are planning on 2" foam board and 5" concrete and packing a little more sand. We are undecided if we should put down a moisture barrier plastic sheeting. Do you have any thoughts on that?
  • Oct 14, 2008, 08:16 AM
    amricca
    You do not need a vapor barrier if the garage is detached and unheated, if there is a chance to may have living space above the garage or want to heat it, you should put in a 6 mil vapor barrier.

    Quote:

    IRC - R506.2.3 Vapor retarder.
    A 6 mil (0.006 inch; 152 µm) polyethylene or approved vapor retarder with joints lapped not less than 6 inches (152 mm) shall be placed between the concrete floor slab and the base course or the prepared subgrade where no base course exists.

    Exception: The vapor retarder may be omitted:
    From garages, utility buildings and other unheated accessory structures.
    From driveways, walks, patios and other flatwork not likely to be enclosed and heated at a later date.
    Where approved by the building official, based on local site conditions