OK, first part.
What you are describing is fine.
Small details: you do not need #4cu to a ground rod (or two) alone. #6cu is all that is required for this. NEC 250.66(A)
Also, the connection to the first rod must be continuous, but the second rod is a supplemental electrode. The wire is not required to be continuous to it, but it is usually easiest to simply loop the wire from one to the other.
Second part, both grounding electrode conductors and water bonds must go to the service disconnect. In your case this is the disconnect outside.
Stan, I can't speak for the NEC on this, but the #4 GEC is required by local code because it is 200 amp service. So, from the ground rods, do I run the #4 to the exterior main disconnect? To be clear, there will be no GEC run to the meter?
IF your water pipe entering the house is metallic, then you must connect to it within 5' of where the pipe enters the house. This wire also serves as the water bond.
If the water pipe entering is plastic then you just have to run a water bond to any accessible spot on a cold water pipe.
This wire is sized according to T250.66.