    Melanie00
    A/C comes on for 3 seconds, shuts off & then starts up again
    I just moved into a new home and noticed that each time the A/C comes on it starts up for about 3 seconds, shuts off, then starts up again. This second start-up is when it stays on until the desired temperature is reached. I have a Honeywell SuperStat thermostat that is about four years old and the A/C unit is about 13 years old. Is this normal?
  • Oct 4, 2008, 06:15 PM
    MarkwithaK

    No this is not normal. We call it short-cycling and it can cause damage to the system.
  • Oct 4, 2008, 07:36 PM
    hvac1000
    Sounds like a defective or out of range low/high pressure control. As MarkwithaK said this can cause damage so have your unit serviced right away.
  • Oct 5, 2008, 08:57 AM
    MarkwithaK

    As hvac1000 said, get it inspected by a local service company. I highly doubt that you have a low pressure control as they are not that common on residential systems but it does happen.
  • Oct 5, 2008, 11:22 AM
    hvac1000
    A run capacitor can also cause this problem. Unit will start but not run. Check wiring to capacitor and compressor in outside unit.
  • Oct 5, 2008, 11:28 AM
    MarkwithaK

    With that old of a system it could also be a weak valve putting a larger load than normal on the system causing the internal overload to open. Could be a weak overload... just way to many options to diagnose without physically being there. Save yourself a ton of headache and call your service company.