  • Oct 1, 2008, 05:57 PM
    dannycar24
    Wayne oil burner air in system
    I have a wayne oil burner in my barn it worked great last year I replaced the electrodes and transformer the end of last winter. Now this year it woudnt light right away so I though it might be low on oil so I filled the small tank I use up and bled the system using the bleeder so air came out then when I closed the bleeder it lit instally. I thought I was done till it tries to start again and it does the same thing again. It will keep running till it shuts off then it won't relite again till I crack the bleeder and let the air out of the pump I have checked and replaced the line and filter I just don't know where the air is coming form does the pump need to be replaced? Any help would be greatly appericated.. Dan
  • Oct 2, 2008, 04:17 AM
    hvac1000
    The pump shaft seal could be bad but any joint or other connection could allow air into the system.
  • Oct 3, 2008, 05:03 PM
    dannycar24
    Yep your exactly right it was the pump seal I replace the whole assembly and it works perfect thanks... Dan
  • Oct 3, 2008, 05:46 PM
    hvac1000
    No problem. Glad you got it going.