    Trane xe80 code 4, no heat
    All summer the cooling worked fine, when I switch over to heat this week, it didn't come on.
    The control box shows a code 4, which says "THERMAL PROTECTION DEVICE OPEN"
    Any help?
  • Sep 30, 2008, 10:13 AM
    hvac1000
    A safety device is open. You will need a meter and track down the defective item. Wiring diagram usually on blower door.
  • Dec 16, 2008, 09:07 AM
    cinwnst
    I had the same code after a lot of looking and figuring what wire goes with what I took the circuit board off and looked at the back it had a burned mark which means the circuit board is bad. It cost me $200.00. I purcharsed a new one and put it in myself works great. Just rememenber when you disconnet the wires and put the new board in you do one wire at a time so you know where they belong!