  • Sep 14, 2008, 01:14 PM
    BrentEdwin
    Separate Grounding Electrodes
    Can I use separate grounding electrodes for my main service box and my subpanel as they are a significant distance away from each other?
  • Sep 14, 2008, 01:30 PM
    stanfortyman
    If they are in the same structure a sub-panel does NOT require an electrode. Only the service equipment does.

    If the sub-panel is in a detached structure it DOES require an electrode (or two).