Hi! I'm at my whits end with this one so here goes...
I'm currently installing recessed fluorescent T8 2-lamp fixtures in my garage, one of which I want to have powered by a Leviton PR180 occupancy sensor. After my initial installation attempt, the fixture flickered and it was then that I noticed that the fixture uses an electronic ballast and the switch is rated solely for magnetic ballasts.
Ok, no problem. I went to RadioShack, got myself a heavy duty relay, and wired everything up such that the occupancy sensor merely operates a relay that, when closed, provides a clean hot lead directly to the fixture.
This fixed the flickering, but now the fixture does not turn off. As it turns out, this occupancy sensor, like most on the market, does not operate correctly unless there is a specific minimum load on it. In other words, the relay coil does not provide sufficient load to allow the occupancy sensor to function correctly. I verified this by splicing a incandescent light fixture on the occupancy sensor in parallel with the relay; when this was done, everything worked as intended.
So the million dollar question... what next? Is there a quick and simple solution for allowing me to use my current fixture as is with the PR180 occupancy sensor? Is there something I can splice onto the sensor to provide ample, yet minimal, load on the line to allow this setup to work? Or should I just bite the bullet and keep trying to hunt down a magnetic ballast? I'm handy with a soldering iron so if there is a special component I could splice onto the line, I'm willing to give it a shot.
Specs on the occupancy sensor:
- Load Rating: 40W/VA Min 500W 400VA Max (per Leviton website)
Specs on the relay:
- RadioShack cat. #: 275-217 DPDT
- Continuous coil voltage: 132VAC
- Power consumption: 1.10VA max
- Rated voltage: 110/120VAC
- Coil resistance: 4.430 ohms max
- Pull-in voltage: 9.6VAC
- Dropout voltage: 36VAC
- Nominal coil current 8.4/9.2mA
- Contact rating: 10A @ 110VAC or 24VDC
- Minimum load 100mA, 5VDC
Thanks in advance for any and all assistance!
-Dan
Comment on Missouri Bound's post
Many new occupancy sensors also include infrared sensors that detect occupancy even if there is no motion. Don't discount all occupancy sensors just because your device was not right for your application.