Originally Posted by speedball1
The correct setting for a bladder tank is 2 PSI under vthe cut in point of the control box. This is set when the pump's shut off and the system's bled down.
Now let's check that bladder tank for a rupturede membrane. There are several ways to test a bladder pressure tank. (1) Open the snifter valve on top of the tank. If water comes out tank's faulty, **OR** (2) Take a metal object and start at the bottom of the tank and start tapping. You should hear a "clunk" until you get about half way up the tank. Then you should hear a "clank".
If you hear the same noise all the way up the tank then it's faulty.
In both cases if it fails (1) and(2) the tank must be replaced. Good luck, Tom