    Rough-in location for dishwasher receptacle
    Installing boxes for kitchen outlets, been so long since last job don't remember d.w. outlet height, am assuming within a few inches of finish floor? Thanks, Ken
  • Aug 30, 2008, 02:16 PM
    Washington1
    There isn't a specific height.
  • Aug 30, 2008, 02:26 PM
    Washington1
    We normally stub-out a wire from the floor, or from the wall. If from the wall, I say it's no more than 6 inches off the floor. I only had to install one receptacle outlet for a dishwasher in my entire career, and in this case I based it on the dishwasher.
  • Aug 30, 2008, 03:04 PM
    stanfortyman
    I either put it horizontal right on the bottom plate (there is no base moulding behind a DW), or I install it in the sink base cabinet and drill a hole to pass the cord through.
  • Aug 30, 2008, 04:24 PM
    donf
    One major concern is that you do not use the small appliance service to supply power for the d/w receptacle. That would be a violation of the NEC code. Also, if you are installing the outlet below and inside of a cabinet, you do not need to GFCI protect the outlet.

    One other thing, if it is at all possible run a 20 amp cable to the outlet and use a single receptacle. Essentially, you would want a dedicated line source from the main panel to the outlet. So you will need a Single receptacle, Single receptacle face plate. #12 AWG cable. Junction box and a 20 amp 120 volt breaker
  • Aug 30, 2008, 05:11 PM
    561packrat
    Quote:

    Originally Posted by donf
    One major concern is that you do not use the small appliance service to supply power for the d/w receptacle. That would be a violation of the NEC code. Also, if you are installing the outlet below and inside of a cabinet, you do not need to GFCI protect the outlet.

    One other thing, if it is at all possible run a 20 amp cable to the outlet and use a single receptacle. Essentially, you would want a dedicated line source from the main panel to the outlet. So you will need a Single receptacle, Single receptacle face plate. #12 AWG cable. Junction box and a 20 amp 120 volt breaker

    Sounds good, but what is the small appliance service? I will follow your suggestion. Thanks, Ken