Originally Posted by massplumber2008
Hi MK..
I didn't think the male adapter was going to thread into that cleanout...sometimes threads at cleanouts don't match any known threads of a fitting to adapt over to pvc because they don't want people threading fittings into them....;)
What fitting is that...? Is that a male adapter or a reducing coupling in the fernco donut?? Is it a street reducing coupling??
If one of the above, as good as it looks, this connection could very well leak later when placed under pressure (such as a full toilet flush). The fernco donuts are made to accept full size pipe not any of the other fittings I mentioned.
You could try installing full size pipe in the fernco donut and then take off with sanitary tee and cleanout from there...Or you could install a manhoff fitting (see picture) and PACK that in using a little oakum and some lead (melt this in ladle or similar tool). Here, you pack oakum around joint to within about 1-1.5" of top of cast hub and then melt/pour lead to rim of cast hub...let cool and then pack the lead tight with packing irons (last 2 pictures). Tools can usually be rented for this.
I hate to be a bummer on you...looks like you did some hard work there...but you asked if this looked like it would work and in my experience the fittings I mentioned first don't work with these donuts!! I would hate for a sewer smell/leak to develop later down the road under that floor....so figure that we should take a little extra time here and discuss this so that we can be sure no issues later...hope you don't mind!!
Let me know what you can...ok??
MARK