    Hi

    I am trying to run this AWG 6-2CU UF-B underground feeder cable from the basement to an outdoor well pump controller. This is a three wire (two isolated + ground) cable that is to be connected at 240Vac from the main panel and routed out for about 200ft. The controller is supposed to limit the current to 20A.
    I had the 18" deep outdoor trench dug, and I would like to protect the cable on most of its outdoor length.
    I read however some post (not on thi site) stating that one cannot run underground wire through conduit on the entire length of the cable because of possible cable outgasing. I still want my cable protected though, for future landscaping projects.
    1. If I want to use some plastic pipe to protect the cable how often should I cut the pipe then? 2. What less expensive options do I have trying to protect the underground cable?

    I am also contemplating running in the same trench (at 8” depth though) an irrigation pipe.
    3. Would this create any issue from an NECode stand point?

    Thank you for help
  • Aug 23, 2008, 01:19 PM
    stanfortyman
    You certainly can put that cable in conduit, problem is it will need to be pretty big, like 1-1/4 or 1-1/2 inch. If it were me I'd use 1-1/2" PVC Sch80.
    6/2UF cable is quite large.

    No problem from an electrical code standpoint to have the water above the electric.