  • Aug 21, 2008, 03:44 PM
    Scrambler81st
    Total Line P374-2800 won't light up
    Help! I am switching from a Honeywell Chron II to a new Total Line P374-2800 and can not get the P374 to light up. Red wire volts read 24vac at wall so am getting proper voltage at stat. HWC II had jumper between R and Rc. Do I need similar jumper on P374? If so, where?
    Have Carrier 2ton a/c split system with 1995 80% Carrier gas furnace

    Here are P374 terms as marked on base plate and schematic.

    (G-fan) (Y1-cool) (W1/O/B-Heat 1st stage) (R-pwr) (C-common) (W1/O/B- Rev. valve) (W2 Heat stage 2) (Misc 1) Misc 2) Misc 3) (RS+5 remote sensor +5vdc) (RS1- remote sensor signal) (RSGND remote sensor ground) (RS2-remote sensor signal 2) (CK1 dry contact switch 1) (CKGRN-dry contact switch 2)
  • Aug 21, 2008, 06:12 PM
    acetc
    This thermostat requires a common wire connected to the "C" terminal where as the old one may not have needed a common wire, no jumper on this thermostat, good luck, Mike
  • Aug 21, 2008, 08:11 PM
    Scrambler81st
    Quote:

    Originally Posted by Scrambler81st
    Help!! I am switching from a Honeywell Chron II to a new Total Line P374-2800 and can not get the P374 to light up. Red wire volts read 24vac at wall so am getting proper voltage at stat. HWC II had jumper between R and Rc. Do I need similar jumper on P374? If so, where?
    Have Carrier 2ton a/c split system with 1995 80% Carrier gas furnace

    Here are P374 terms as marked on base plate and schematic.

    (G-fan) (Y1-cool) (W1/O/B-Heat 1st stage) (R-pwr) (C-common) (W1/O/B- Rev. valve) (W2 Heat stage 2) (Misc 1) Misc 2) Misc 3) (RS+5 remote sensor +5vdc) (RS1- remote sensor signal) (RSGND remote sensor ground) (RS2-remote sensor signal 2) (CK1 dry contact switch 1) (CKGRN-dry contact switch 2)

    Thanks, Mike. For clarification purposes, you are saying that I need to have a wire run from "C" on the air handler (furnace) computer board to "C" terminal on P374?. and DO NOT even attempt to use a jumper on P374?
  • Aug 22, 2008, 05:51 PM
    acetc
    Yes that is correct. Mike