    ChiefBrody
    Fan in AC unit doesn't turn without assistance
    I have a Trane unit outside. When the air cycles, I have to get a screwdriver and give the blade a little nudge for it to turn. It's fine until the unit cycles off again. I looked at the run capacitor and didn't see any bulges. The condenser and everything else works fine.

    Does this sound like the fan motor is going bad or the capacitor is bad, or something else?
  • Aug 20, 2008, 06:36 AM
    Credendovidis
    Hello ChiefBrody

    All indications are that either the capacitor or the start winding of the motor are faulty.
    Your actions with the screw driver supports that.
    Difficult to check the capacitor, but if you have a multimeter it is easy to check the motor.
    Any motor measurements should have course be done with both the power first and the motor later completely disconnected. Both points that are normally connected to the capacitor should have a similar resistance in respect to the point that is normally connected to the neutral.

    Take it from there. If need be, take the capacitor with you to the repairshop to be tested. 95% chance that is the guilty part !

    Success

    :)
  • Aug 20, 2008, 08:20 AM
    esquire1
    Long story short, capacitor is bad. Replace with like value
  • Aug 20, 2008, 06:48 PM
    Missouri Bound
    I would suggest you replace the capacitor first, before taking the motor out. If it still doesn't work, then remove the motor... troubleshooting starts with the simple things first.