  • Aug 16, 2008, 07:45 PM
    painted4love
    Wiring for a switch at the beginning of a run.
    Setup


    Circuit-----------to switch-----to
    ---Receptacle--Receptacle--Receptacle--Receptacle

    How do I get the switch to run 1/2 of the first and 1/2 of the last receptacle only? Is there a way?

    Or should I run separate power supply to the receptacles that I want on the switch?

    I know there is an easy way but is there a way to do the other if its all connected in the same rung.

    Right now the switch has not been incorporated. I am trying to get light into the room and working off a switch to a receptacle seems like the best way.

    Is it going to be to difficult to wire since the switch is at the start of the run?

    Any ideas would be great..
  • Aug 16, 2008, 08:35 PM
    hkstroud
    2 Attachment(s)
    ..
  • Aug 17, 2008, 07:33 PM
    painted4love
    Quote:

    Originally Posted by hkstroud
    ..

    This is the setup from the breaker (can I use a 20amp on this circuit?)

    15amp (20amp?)
    12/2 (black/white/copper)
    To

    Switch and then 4 receptacles

    I'm confused as far as do I need to change wire once adding a switch? 12/3? To incorporate the red wire?
  • Aug 17, 2008, 08:51 PM
    hkstroud
    If 15 amp breaker, use 14-2 to switch, use 14-3 to outlets.
    If 20 amp breaker, use 12-2 to switch, use 12-3 to outlets.

    Both 14 and 12 gauge wire is available in 3 conductor (black, red, white, ground) cable.

    Be lot of wire in each box, get deepest boxes available. 14 gauge is lot easier to work with.