After replacing a blown running capicitor on the outdoor unit I have power to the contactor but the unit won't come on when the thermostat calls for cooling. I can manually engage the contactor and the fan and compressor come on. I had no meter to check the power to the coil so I plan to do that next and assume a bad coil if power is there. If not then I assume either the thermostat or the 24v transformer. Am I missing anything?