20 year old GMC 5 ton unit. Manual fan switch turns fan on, but in auto position the fan intermittantly will not come on, or shut off. I am operating the AC unit with the fan switch on all the time.
![]() |
20 year old GMC 5 ton unit. Manual fan switch turns fan on, but in auto position the fan intermittantly will not come on, or shut off. I am operating the AC unit with the fan switch on all the time.
Sounds like a relay switch plumb wore out and needs replaced.
I would suspect the thermostat, but it somewhat depends on the thermostat design. In AC mode the thermostat controls the fan.
So, the tstat must have a relay to turn on the fan.
If the tstat is designed such that it activates that relay in AC mode, then it doesn't make sense.
But if there is a real physical switch that bridges the relay contacts, then the diagnosis makes sense.
Checking, depends on your skils and if you own a multimeter. Do you?
The tstat is Robertshaw; but with the old mercury switch tstat, I sometimes would have to manually cycle the switch to get the blower to turn off.Quote:
Originally Posted by impac41
Now when the tstat is in auto, the compressor and condenser fan will come on, but the blower will operate intermittantly; sometimes it will come on or go off with the unit, sometimes it will not. I disassembled the relay, it looks fine inside. The relay is energized with 24vac manually through the tstat switch, or automatically from some other switch or relay; I haven't been able to locate that source to check for 24vac.
Look here: Thermostat wiring code
You need to look at the voltage between R and G when the system screws up.
It wlll be 24 VAC if it screwed up and near zero volts if the relay in the stat is closed.
There could be 3 things that control the fan:
1) A switch on the tstat (not always)
2) A relay in the tstat
3) A relay in the furnace
I'm suspecting the stat relay.