  • Aug 2, 2008, 10:15 AM
    prakashpbt
    Load calculation
    Respected sir I amprakash ihave doubt regarding load calculation.

    I have a 5 amp socket (ups power ) .can I connect 5 computors to that socket through extension box.please explain me any body knows
  • Aug 2, 2008, 12:28 PM
    tkrussell
    Need to know the load in amps or watts of each computer. If the total exceeds 5 amps, then, no.

    If in the USA, and possibly elsewhere, the receptacle may need to be derated, here in the US we derate certain things by 80%.

    Also need to know the wattage, amperage or volt-amps output capacity of the UPS , to be sure it is not exceeded.
  • Aug 2, 2008, 12:50 PM
    DrLang
    As the reply before me states, this will depend a lot on the computers. However, unless you dumped a lot of cash on that UPS, 5 computers (unless they're laptops or other ultra low power systems) will probably kill it before you can snap your fingers. The battery just doesn't have that kind of capacity.