    Do all toilets set 12" from the wall to the flange bolts? How much fall is needed for the 3"drain to the septic tank connection?
  • Jul 14, 2008, 06:52 AM
    hkstroud
    The most common toilet is built for a 12" rough in from finished wall, however 11" and even 10" rough in toilets are available. Drain lines should have a slope of 1/8 to 1/4" per foot. Not less, things don't drain. Not more, water runs away leaving solids behind.
  • Jul 14, 2008, 07:07 AM
    Milo Dolezal
    3" pipe should slope at 1/4" per foot. 4" is 1/8" per foot.

    As Harold correctly states toilet setting measurement varies. Manufacturers recommend 12". We routinely rough-in our toilets at 11 1/2" away from finished wall and still have 1" space between tank and wall.
  • Jul 14, 2008, 08:09 AM
    ballengerb1
    The above answers are right on the money. If you were in a bind there are even a few 9" toilets but 12" is the most common. You must also be 15" on center off any side walls to be within code.