Condenser fan motor issues
I have a rheem central a/c unit (2 tons) that I have been knocking my head on. The fan keeps shutting down about 15 to 20 minutes after the unit has been running and trying to cool my house. I have checked the voltages on the leads to the fan and compressor and the leads to the relays from the breaker board to unit. At first I thought it was the fan motor sticking it's last leg, however, I noticed that when I would shut down the unit manually for a couple of minutes and then re-start it, the fan would come back on. I have checked all the wiring and all seems good. The unit is about 11 years old. I have cleaned it and checked for leaks. I did notice when taking voltage readings from the relay to the capacitor and to the motor and compressor, on one of the leads goind to the fan motor, it would drop from 271volts from start and then it will drop down to 157 and the fan will slow until it comes to a stop. This reading was from the capacitor to the fan motor. The other lead from the capacitor to the compressor remained the same.
Can you please help!
Thank you
Joseph :confused: